Attached is tank readings graph. AttachmentUnleaded Tank levels Graph 10_15 through 10_23 Actual vs Probe.pdf (244 Downloads) |
10/25/2013 7:22 AM | |
Posts: 93 Rating:
|
Dear Ekersey, Can you write what parameters are entered under P001, P003 ..... P007? Regards, Davinder Singh |
10/25/2013 6:24 PM | |
Posts: 5 Rating:
|
Plan to get these settings tomorrow morning. Thanks. Ed |
10/26/2013 6:36 PM | |
Posts: 5 Rating:
|
P001 = 1 (Level) P003 = 1 (Slow response) P004 = 4 (units = feet) P006 =18.75 ft P007 = 18.0 ft |
10/29/2013 3:31 PM | |
Posts: 5 Rating:
|
Wow and thanks. Attached is drawing of the "float/tape" set up. It appears the float is more of a pancake shape than a sphere. Regardless, your evaluation seems much more plausible. Will try what you suggest and post results. We are only able to change parameters with the Siemens hand held remote and have to use manlift. Unable to change with HART communicator on ground. So it may take me a week or so to schedule manlift/get done. Again, thank you for your evaluation and time. Ed No change in reading when pulled float up on Unleaded tank on 10/29/13. Next step = schedule sonic probe (velocity) calibration per recommendation above. Ed AttachmentMOORMANN STORAGE TANK GAUGE.pdf (251 Downloads) |
Last edited by: ekersey at: 12/17/2013 5:42 PM |
|