Hi, the current configuration of reference junction "fixed reference temperature" with "0°C" will not work. Please check which BaseUnit is used. If you have a BaseUnit "type A1", please use internal reference. If you use an BaseUnit "type A0", you will need an external reference via an additional PT100. There are some more dependencies besides that, but you can also check thes FAQ. What do you have to watch out for when using thermocouples if the expected value is not displayed?regards sancruz |