2/8/2016 11:52 AM | |
Joined: 3/14/2008 Last visit: 2/27/2025 Posts: 2172 Rating:
|
There is no standard block for this... What you can do is the following: 1. Create a CFC chart where you put two VlvL blocks in it. 2. Go to the block folder of your project and go to FB1899, which is the VlvL block. 3. Copy all inputs, in/out and outputs and copy them in the Chart I/O, see next step 4. In CFC, select View->Chart I/O's and copy all the inputs, in/out and outputs. 5. Connect all inputs to the first VlvL block. 6. Create a copy of all inputs, in/out and outputs and rename those to for example: OpenAut_2. 7. Connect all modified parameters the second VlvL block. 8. You can now compile this CFC chart as block type. For this, go to CFC chart and select Chart->Compile->Chart as block type. 9. Fill in necessary data such as block number and create the block. 10. Now you can insert the new generated block in a new CFC chart, where you connect your input/output driver blocks and logic. 11. You can create a copy of a block icon of the type: VlvL and modify it, so you have 4 feedback signals, 2 outputs etc.. |
Last edited by: Oreca at: 2/8/2016 11:54:46 AMLast edited by: Oreca at: 2/8/2016 11:55:13 AMIf I could help you, you can use the RATE button. Thank you. |
|