Hey guys, we have a configuration as shown in “ figure_1” but for some reason(don’t ask why J) we want to temporary change the configuration to the “figure_2” and use a CPU 414H as a normal CPU (not a redundant CPU) and my question is, is this doable? Can we use a 414H CPU as a normal CPU? We haven’t bought the modules yet but I made a configuration like “figure_2” in “HW Config” in SIMATIC manager and I didn’t get any inconsistency error after hitting “save and compile” button. AttachmentConfiguration.zip (471 Downloads) |
Last edited by: Ariya Man at: 7/8/2013 9:04 PMLast edited by: Ariya Man at: 7/8/2013 2:57 PM |
|
7/8/2013 2:17 PM | |
Joined: 11/8/2011 Last visit: 11/5/2024 Posts: 387 Rating: (43) |
Hi Hardware configuration must be done s7400 station not in H station Hope this helps |
7/8/2013 3:05 PM | |
Posts: 559 Rating: (87) |
Dear Ariya Man, As you already come to know that you can use this CPU as a stand alone. No problem at all. But in this case remove One IM from the Remote I/O Rack. No need to put 2 IM if you are using stand alone system. Also no need to use active back connectors also if you are using just for training purposes. |