Hello fabioga66 How did you implement the I/O module and the remote station? By GSD file? In that case the modul driver wizard will not consider them, because only modules listed in the document "SIMATIC Process Control System PCS 7 Released modules" are supported by the modul driver wizard. I'm not familar with VIPA, but I once heared that their concept was (or maybe still is) that their components are compatible to Siemens modules. In that case you configure the corressponding Siemens hardware in your project, but in reality you use VIPA components. If you find a compatible Siemens component to your VIPA component in the document "...Released modules" you configure this and if you can do this for all the VIPA components (IM and I/O-modules), then the driver wizard would work. So to answer your question: By default the channel driver where you connected the symbol which is causing that warning will not work. But you could configure the input "Mode" manually. Of course by this you won't get any diagnosis of the hardware, but at least you could use functions of the channel driver like scaling (analog input driver) and/or simulation. Best regards... |
Last edited by: mark1507 at: 04/05/2022 13:09:05"Expert" does not necessarily mean Siemens employee. Please cross-check your requirements always with official Siemens documentation. Also "Experts" are pleased about feedback. Please don't send support requests as PM. Questioners who don't follow up their thread will be put to my list of users to be ignored. |
|