10/9/2008 5:49 PM | |
Posts: 328 Rating: (29)
|
Dear Sir Which system are you having problems with and what machine data are youtrying to change? Regards SteveJ |
10/10/2008 5:28 AM | |
Posts: 16 Rating: (0) |
Hi, I use Sinumerik 802D and baudrate profibus of Simodrives is 12Mbaud but baudrate profibus of Sinumerik 802D is 9Mbaud( it is protected). So itshowsan error when transfering data( error no. 26102 Axis Z1, drive 2 Sign of life failure) . I checked the Simodrives axis Z,X and SP by SimoComU. they is good and dispaly alarm show "RUN"). I haveanother Sinumerik 802D and it is good. I checked baudrate profibus and it is 12Mbuad. Why is baudrate profibus of Sinumerik set to 9 Mbaud? Can you help me? Thanks |
10/10/2008 11:19 AM | |
Joined: 9/18/2006 Last visit: 9/2/2024 Posts: 591 Rating: (64) |
Hi. I have looked my data of a drive. There can be it to you will help. Successes. |
10/10/2008 12:11 PM | |
Joined: 1/29/2008 Last visit: 7/26/2022 Posts: 419 Rating: (19) |
Hi Try to read chapter 3.6 from "Commissioning Manual" in this link http://support.automation.siemens.com/WW/view/en/28531038 Best Nit |