10/31/2016 9:29 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
hi,
is there anything loaded on the CPU? you need to load a valid HW-configuration and a program to the CPU. regards, |
FCK WAR! |
10/31/2016 9:33 AM | |
Joined: 5/12/2006 Last visit: 7/17/2024 Posts: 22317 Rating:
Hi, HW Config should be loaded because the Opton handling is enabled, this is only possible with a loaded HWConfig. But if this Option is active you need a program in the startup to activate a valid data set for Option handling. If you need no option handling deactivate the option in the PLC Porperties and download the Project to the plc.
Christoph |
4 thankful Users |
6/28/2021 8:11 AM | |
Joined: 10/22/2013 Last visit: 6/16/2024 Posts: 8 Rating:
In PLC properties/Configuration control, the tick mark in "Allow to reconfigure the device via the user program" must be removed. |
8 thankful Users |
1/20/2022 5:15 PM | |
Joined: 3/19/2020 Last visit: 3/13/2023 Posts: 1 Rating:
Thank you |
2/16/2023 4:50 AM | |
Joined: 12/28/2022 Last visit: 1/20/2024 Posts: 2 Rating:
Thank you so much!!! |
6/18/2024 10:11 AM | |
Joined: 4/28/2015 Last visit: 7/3/2024 Posts: 1 Rating:
thanks |