2/22/2018 7:04 PM | |
Posts: 7 Rating: (0) |
------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 2/23/2018 12:27:54 PMNew subject after splitting |
|
2/27/2018 3:20 PM | |
Joined: 1/30/2006 Last visit: 9/16/2024 Posts: 310 Rating: (59)
|
Try to Look in the Device configuration under Pulse generators. |
BR. Sven |
|
5/23/2018 11:06 AM | |
Joined: 9/1/2006 Last visit: 11/18/2024 Posts: 193 Rating: (13) |
Yuvaraj does it work now ? I want something simulair... |
5/25/2018 4:50 PM | |
Joined: 10/7/2009 Last visit: 9/9/2024 Posts: 266 Rating: (92) |
Dear Yuvaraj.T, The steps for configuring the S7-1511C-1PN PTO are as below:
Best regards, Yu-wen AttachmentS71511C_PTO_Demo.zip (1173 Downloads) |
Last edited by: Yu-wen Tang at: 5/29/2018 5:12:18 PM |
|
This contribution was helpful to1 thankful Users |
5/25/2018 5:05 PM | |
Posts: 2826 Rating: (687) |
OFF-TOPIC
Could I interest you in the using the software ShareX? Thanks for helping. |
5/26/2018 3:32 AM | |
Joined: 10/7/2009 Last visit: 9/9/2024 Posts: 266 Rating: (92) |
For CPU 1511C-1 PN/CPU 1512C-1PN, the pulse output channels for the pulse generators (PTO) are controlled using Motion Control via the technology objects TO_SpeedAxis, TO_PositioningAxis and TO_SynchronousAxis. For a detailed description of the use of motion control and its configuration, refer to the S7-1500 Motion Control function manual (https://support.industry.siemens.com/cs/document/109749262/) and the STEP 7 online help. See attached for the parameters which must be configured. Best regards, Yu-wen AttachmentCPU 151xC-1 PN Motion Control.pdf (1119 Downloads) |