9/6/2022 4:55 AM | |
Joined: 6/22/2022 Last visit: 4/24/2023 Posts: 5 Rating: (0) |
TIA Portal V17. I have 2 CPU319F-3, each connected to one of the modules. |
9/6/2022 9:01 AM | |
Joined: 1/21/2013 Last visit: 4/26/2024 Posts: 2714 Rating: (440)
|
Hi pavlovand, to me, it looks like you are working on a redundant configuration like a redundant DP/PA link. This is for "Software redundancy for SIMATIC S7" or for "Fault-tolerant systems S7-400H". Since TIA Portal does not support either of these, I'm pretty sure you can't configure the hardware in TIA Portal. Nevertheless, I recommend to create a new support request to clarify the behavior. Kind regards |
9/7/2022 7:04 AM | |
Joined: 10/7/2005 Last visit: 4/26/2024 Posts: 3004 Rating: (1046) |
Hi pavloland as Stefan already said, what you are trying to do is in principle possible with your S7-300 CPU's in a so called "Software Redundant System". The two problems you have with your setup are this though:
See also THIS link for more and note that it also contains a link for the Software Redundancy Manual |
Last edited by: fritz at: 09/07/2022 07:05:41Last edited by: fritz at: 09/07/2022 23:26:59Cheers |
|
This contribution was helpful to1 thankful Users |
9/7/2022 11:31 PM | |
Joined: 10/7/2005 Last visit: 4/26/2024 Posts: 3004 Rating: (1046) |
Correct in principle, but the CP343-2 is NOT supported in an ET200M of a Software Redundant system (I edited my previous post though to remove this ambiguity). |
Cheers |
|
This contribution was helpful to1 thankful Users |