6/4/2018 2:41 PM | |
Posts: 13 Rating: (0) |
Good afternoon. I was out of order CPU 315-1AF03-0AB0. There are CPU 315-2 DP 315-2AG10-0AB0 in the presence. Can I use it? |
6/4/2018 3:19 PM | |
Joined: 11/29/2011 Last visit: 4/24/2024 Posts: 1354 Rating: (229) |
Hi, The 6ES7315-1AF03-0AB0 product page does not say that 6ES7315-2AG10-0AB0 is a successor product. Anyways if you open HW config and "Right Click"->"Replace Object" then you can see the 6ES7315-2AG10-0AB0 part coming up. Without knowing the application it is hard to say, but probably all right if you update the HW config with the right CPU. It is always a good practice to keep using supported hardware elements so you can make like like for replacements. It is not the case there. Keep in mind that 6ES7315-2AG10-0AB0 is already discontinued the current part is 6ES7315-2AH14-0AB0. See the bellow 2 relevant articles: Type Discontinuation of S7-300 CPUs 313, 314, 315, 315-2, 316-2 Product Information for S7-300 CPU's 312, 314, 315-2 DP and 315F-2 DP |
- What you read here, please check with manuals and your requirements. |
|
This contribution was helpful to3 thankful Users |
6/6/2018 6:43 AM | |
Posts: 13 Rating: (0) |
Thanks to all. I replaced the PLC. He approached without comment. |
Follow us on