Hello cuongaz80, The permanent self-monitoring feature of 3UG4625 ensures reliable system monitoring.The connected 3UL23 residual current transformer is also permanently monitored for open-circuit or short-circuit. The 3UL23 Transformer connecting cables must be twisted and not routed in parallel to live cables to protect from emitted interference. Keep the length of the connecting cables to a minimum.The resistance at the transformer connecting cable must not exceed 5Ωto ensure correct fault current monitoring. If you have furthermore the problem, please contact our Siemens Technical Assistance Support (technical-assistance@siemens.com). BR |