Joined: 9/21/2006 Last visit: 5/25/2023 Posts: 247 Rating: (65) |
The behavior of I/O under various conditions is discussed in SIMATIC S7-400 S7-400 Automation System Module Data: Effect of supply voltage and operating mode As I understand your system, you have AQ modules in the central racks of your S7-400H system. Since the AQ module for the S7-400 central rack I/O (6ES7 432-1HF00-0AB0) does not support a substitute value, then the output value from the card if the local CPU fails but power is still applied to the module will be the last value before failure. If power is lost to the module, the output value will be 0. |
4/6/2022 1:56 PM | |
Joined: 5/16/2018 Last visit: 1/17/2024 Posts: 30 Rating: (0) |
Thank you :) will check the link. In my case the signal will freeze then. |