8/21/2013 2:09 PM | |
Joined: 1/5/2013 Last visit: 5/3/2024 Posts: 10 Rating:
|
Hi every body We´re commissioning ET200S Analogic module 6ES7134-4FB01-0AB0and we havent got any value in the analogic aoutputs. In the Hardware configuration we have assigned one word for each output. QW358 for analogic output 1 QW360 for analogic output 2 If we write (in DEC+/-) some value in QW358 we get no value in the output . Is it necessary some extra configuration or use some instruction to write analogic output?? Thanks!!! |
8/21/2013 2:14 PM | |
Joined: 1/28/2012 Last visit: 7/23/2024 Posts: 519 Rating:
|
It is analog Input Module (Voltage Type). . |
Regards, |
|
8/21/2013 2:41 PM | |
Joined: 1/21/2013 Last visit: 6/6/2024 Posts: 4620 Rating:
|
Hi you need at least the 6ES7 135-4FB01-0AB0, which is 2 analog voltage outputs and NOT 6ES7 134-4FB01-0AB0. |
8/28/2013 6:28 AM | |
Joined: 1/5/2013 Last visit: 5/3/2024 Posts: 10 Rating:
|
Hi I wrote trw worng reference, i have an analog output6ES7135-4FB01-0AB0, but i think that I managed the problem. I use peripheral access. Move MW300-->PQW2000 Move MW302-->PQW2002 Do you know if exist some instruction to scalate these signals?? Thanks!!
|
8/28/2013 9:13 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating:
|
Hello, For scaling/unscaling you can use FC105/106. You will find them in the standard library-->TI converting blocks. Regards, Marcjan AttachmentFC1-scale-unscale.pdf (195 Downloads) |
Problem solved? |
|