Industry Online Support
Technical Forum
7/5/2012 7:41 AM | |
Posts: 211 Rating:
|
Hi all! I am little confused. They say that I need: 7KM9300-0AE00-0AA0 - PLUG-IN COMMUNICATIONS MODULE SWITCHED ETHERNET PROFINET to make PAC3200/4200 a Profinet IO device, to be easily used in S7 systems with profinet IO controllers (S7-1200/300/400). But, in manuals of PAC3200/4200 THEY SAY THAT SUCH MODULE DOES NOT EXIST! (see picture attached). So, is it possible to use 7KM9300-0AE00-0AA0 to make PAC a Profinet IO device, so it can be connected to S7-1200 Profinet IO Controller? Anyone tried? Thanks! AttachmentProfinet forum.pdf (341 Downloads) |
7/5/2012 8:44 AM | |
Posts: 50 Rating:
|
Hello The SENTRON PAC3200 and PAC4200 has a integrated ethernet interface with a MODBUS TCP protocol. S7-300 and S7-400 has no standard function blocks for this communication protocoll. Here can you use the "OPEN MODBUS" blocks. http://support.automation.siemens.com/WW/view/en/22660304 Or the s7-1200 controller, only the s7-1200 has standard modbus blocks integrated. If you likea PROFINET protocol communication, then require this an additional expansion module 7KM9300-0AE00-0AA0 Switched Ethernet Profinet. |
7/5/2012 12:54 PM | |
Posts: 211 Rating:
|
Thanks. So, you tell that 7KM9300-0AE00-0AA0 is connectable to PAC3200/4200 and makes PAC a Profinet IO device, which can be connectet to sa Profibus Controller. I know about Modbus TCP via intergated portand i make it work with S7-1200. Now I need Profinet solution to connect 16 PACs and acheive more grequent data enchange. |
7/5/2012 1:19 PM | |
Posts: 50 Rating:
|
Hello ******** So, you tell that 7KM9300-0AE00-0AA0 is connectable to PAC3200/4200 and makes PAC a Profinet IO device, which can be connectet to sa Profibus Controller. ******** I think here is a mistake. If you use the 7KM9300-0AE00-0AA0, then is there no gateway connection toPROFIBUS. The 7KM9300-0AE00-0AA0ist only for PROFINET. |