11/4/2020 5:49 PM | |
Joined: 4/28/2015 Last visit: 10/22/2024 Posts: 1278 Rating:
|
Hi, yes this is possible. p2507 is the parameter to set if you want to start an absolute encoder adjustment (p2507 = 2). In p2599 you can set the reference coordinate before. And afterwards don't forget to copy Ram to Rom to save the encoder offset value retentively. Making it simple for you - there is a ready to use PLC block which does all the steps for you: https://support.industry.siemens.com/cs/de/en/view/109760317 |
Best regards, |
|
This contribution was helpful to
1 thankful Users |
11/5/2020 5:47 PM | |
Joined: 1/17/2006 Last visit: 1/14/2025 Posts: 554 Rating:
|
Hi ! Thank you for the reply and information but unfortunately I'm using Sinamics with PCS7 v.7.1. Best regards, Berg
|
"Educate the children and it won't be necessary to punish the men." |
|
Follow us on