6/18/2007 4:47 PM | |
Posts: 102 Rating: (1) |
Is there a function or a script to acknowledge all active alarms displayed in one "Alarm Control"; I need to implement this in an action. |
6/20/2007 8:47 AM | |
Posts: 1084 Rating: (72)
|
Thanks for the reply danielle. Missed that "displayed" my self. with regards, Ikkezelf |
7/2/2010 6:42 PM | |
Posts: 510 Rating: (117) |
I had a customer that recently wanted the same feature. The US WinCC Center of Competency help me with this. The Group Messages in Alarm Logging lets you treat the Error Message Class like a custom class.From the properties you can specify anAcknowledge tag, internal or external.Then with a buttonon a screen or the PLC, you can acknowledge all of alarms ofthat class. You can do this for just one oftypes within a class. I have attached a brief document with a screen capture. Good Luck billwest Attachmentacknowledge_all.pdf (633 Downloads) |
This contribution was helpful to1 thankful Users |