3/8/2007 11:33 PM | |
Posts: 112 Rating: (10) |
You need to read the time from the OP to a data area in the PLC, once that is done you transer the time from the data area to the PLC clock. See attachment which has some custom FC's to deal with the task, the main code is in FC2, you will need to set up area pointers in the OP for job mailbox and date/time. I have used this with an OP270 and CPU315, I'm not sure if there are any great differences to your system. AttachmentOPTimeTr.zip (877 Downloads) |
3/9/2007 9:44 AM | |
Joined: 4/24/2006 Last visit: 10/14/2024 Posts: 8745 Rating: (1168) |
Hi Colin, Here are some links, that can help you: When you use Protool: http://support.automation.siemens.com/WW/view/en/24079457 When you use WinCC flexible: http://support.automation.siemens.com/WW/view/en/24104104 Best regards, Wizard |
6/9/2015 1:28 PM | |