Hi HugoD, I had same problem, and i tried to fix it like you. The difference is that I am using Simatic Box IPC827D with CPU 1507S (F) in TIA Portal v14 SP1, also i dont have ET200 (is it necessery?) I followed your procedure and did everything like you. When i tried to download hardware configuration, PC was restarted. After restarting PLC has no configuration and i lost network driver for X2 port (Intel(R) Gigabit Network Connection). I tried to reinstall driver, but it still doesn't exist in device manager. Do you have some idea how to solve this problem? Best Regards. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 6/29/2017 12:51:11 PMNew subject after splitting |
|
6/29/2017 12:56 PM | |
Joined: 5/12/2006 Last visit: 11/29/2023 Posts: 21947 Rating:
|
Hi, can it be that you assign the X2 to the PLC in the station configuration? Christoph |