Hello Are you sure about version of Protool. Look at Which Engineering Software can be used with which panels?. Anyway about alarms. Make in Step7 one data block, which will contents all alarm condition. (For example: LOW OIL LEVEL (DB1.DB0.0 - connected in program with some level detector.) In Protool open Messages - Alarms and write every message alarms from DB. After that add in Area Pointers new one Alarm Messages and assign PLC and DB that conetens alarms from PLC program. Hope this helps. regards |