10/24/2017 6:50 AM | |
Posts: 31 Rating:
|
Dear Cs team, Pls tell me how to use ALM as a SLM. |
10/24/2017 11:11 AM | |
Joined: 10/11/2006 Last visit: 3/29/2023 Posts: 5467 Rating:
|
Dear kamal.mbc, please set p3400.0 "smart mode" to ON. With this setting the ALM behaves like a SLM in grid commutated operation. Additional I recommend to activate "extended smart mode" via parameter p3440.1=ON. This setting reduces internal losses especially in partial load operation. Additional information is given in List manual referring to mentioned parameters: https://support.industry.siemens.com/cs/ww/en/view/109739998 |
With best regards, |
|