I found the article in English! One thing though that is not clear, is that the siemens analog input module itself is limited to 27648. Anything above that is outside nominal and is over-range and overflow. With that in mind, do we still put 16bits as the number of inputs? When we put TRUE for has overflows, does it automatically detect to 27648? thanks for your help!
------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 07/27/2023 09:35:23New subject after splitting |
|
7/27/2023 10:02 AM | |
Joined: 1/21/2013 Last visit: 11/12/2024 Posts: 3259 Rating: (507) |
Hi jking3, The analog input module can report values greater than 27,648 (= 0x6C00). However, the S7 analog value is designed so that the nominal range ends at 27,648. Please refer to "Representation of analog values". If you have further questions about a specific device, please provide more details. Kind regards |