9/10/2008 8:34 AM | |
Posts: 2930 Rating: (432)
|
Hi, here adiitional notes to marcsinclairs post: 1. Unused analog inputs must be short-circuit. 2. Use shilded wires for your analoge sensor, grounding only at one side 3. Check if your analoge wiring is in parallel to high voltage/current wires. If so, change it Do you have ASi-Master, or SIWAREX modul connected to S7-200? If so, then use the right analoge chanel because this two modules use analoge I/Q to communicate to the PLC. Here an older but still actual FAQ from Siemens: http://support.automation.siemens.com/WW/view/en/2415890 I hope this helps. Helmut |
9/10/2008 9:39 AM | |
Joined: 9/7/2007 Last visit: 8/30/2023 Posts: 550 Rating: (61) |
Hi Gordon, I faced this problem once ago and I connected the shield the M and the result was good |
Best Regards |
|
1/25/2010 11:14 AM | |
Joined: 1/25/2010 Last visit: 4/3/2024 Posts: 2 Rating: (0) |
I faced this problem too, hope this way can solve mine. |