1/19/2020 10:17 PM | |
Posts: 3 Rating: (0) |
Good I have an analog input, a photocell, which controls the voltage of an analog output. This analog output has to output 2 fixed voltages (5V and 10V) as ordered by the sensor. The photocell is: http://ergiocontroles.com/producto/sistema-de-seguridad-y-control/brahma-fc-8/ Is this possible? If yes, what would it be like? Regards, thanks. |
Last edited by: Jen_Moderator at: 01/20/2020 12:09:05Edited text for better reading. |
|
1/20/2020 5:22 AM | |
Joined: 12/18/2014 Last visit: 11/13/2024 Posts: 34207 Rating: (4261)
|
Hello malolokiller, at first welcome to the Forum.
Not everyone in the form speaks Spanish, so the link is not very helpful for most. |
1/20/2020 6:02 AM | |
Joined: 12/27/2018 Last visit: 10/2/2024 Posts: 510 Rating: (43) |
Yes. Your input is analog flame detector with 4-20mA will give INT raw value 0-27648 to PLC . You can scale it to engineering value and generate alarm a set point. Also Unscale for 5V OR 10V and connect to analog output . |
Jinson James, M.Tech (Power Electronics and Power System), |
|
1/20/2020 6:06 AM | |
Joined: 12/18/2014 Last visit: 11/13/2024 Posts: 34207 Rating: (4261)
|
You don't know LOGO!, right? LOGO! analog inputs makes no INT values 0-27648. LOGO! inputs makes 0-1000 units. |
This contribution was helpful to1 thankful Users |
1/20/2020 8:35 AM | |
Posts: 4 Rating: (1) |
Yes, you are right, thats why I wrote ''...check the hardware inside LOGO!'' Hope the malolokiller will solve the problem after this |