Do Siemens have a guide to shielding 4-20mA cables connected to S7 analogue inputs? Thanks. |
8/18/2013 5:22 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715) |
Hello, There is mutch to find in the S7-1200 System manual Shield should be grounded as close to the Module as possible, star grounding is prefered. If possible CPU and sensor supply must be the same. Regards, Marcjan |