Hi, Another option you have is to simply configure this from within the I/O editor of the controller. Please refer to the attached screen dump (Capture1.png). This can be done with on-board digital outputs, or when using TXM1.6R modules. A detailed guide on the properties of the point in the I/O editor is available in the help files. Capture2.png shows the location, and then look for Additional properties for signal type "3-point control, 2 channels". When added within the TIA tool, you will have a single block that you can link to your PID output. Regards, AttachmentCaptures.zip (243 Downloads) |