8/18/2015 7:13 PM | |
Joined: 7/29/2012 Last visit: 4/29/2024 Posts: 3 Rating: (0) |
How can I assign profibus node address by S7 hardware of a R series profibus Temposonics?. I am using s7-400, 416 -2DP CPU. Anybody can help me?. ------------------------------------------------------------------------------------------ |
Last edited by: Shipon at: 8/18/2015 7:16:57 PMLast edited by: Min_Moderator at: 8/19/2015 10:48:27 AMNew subject after splitting |
|
8/19/2015 11:16 AM | |
Joined: 1/28/2009 Last visit: 9/10/2024 Posts: 6849 Rating: (1365) |
Dear Shipon ,
First of all, check gsd of the slave if it supports this capability and to do you need a Class 2 master .Check the page 22 of the manual in attached file and also this old thread: Profibus SSA(set slave address) functionI hope this helps, hdhosseni AttachmentProfibus.pdf (375 Downloads) |
3/18/2018 10:44 PM | |
Joined: 1/23/2013 Last visit: 8/21/2024 Posts: 38 Rating: (1) |
You can use CP5711 and Simatic Manager for setting Profibus address. |