10/12/2021 8:47 AM | |
Joined: 10/7/2005 Last visit: 10/14/2024 Posts: 3024 Rating: (1054) |
A couple of options come to mind: 1.) Install SINEC PNI (the successor to the Primary Setup Tool) on the Panel PC and use it to assign Device names (or any other too that supports PROFINET DCP). Downside is that you need to know and manually match the TIA Portal configured Device name 2.) Do it indeed fully automatically via "Automatic commissioning of a PROFINET IO system" which also caters for device replacement in the future without the need to assign a device name. Usage of managed switches with LLDP support and a configured Topology are a must have for this to work and the two links below have all the details |
Cheers |
|
This contribution was helpful to1 thankful Users |
10/12/2021 1:48 PM | |
Joined: 10/1/2020 Last visit: 2/3/2024 Posts: 4 Rating: (0) |
You got it, thank you for your answer, I'm going to test this option and see which is best suitable for my application. If works, I let you guys know. |
This contribution was helpful to1 thankful Users |