10/22/2017 2:53 PM | |
Joined: 9/27/2006 Last visit: 9/16/2024 Posts: 12282 Rating: (2683) |
Hello mafa; A manufacturer will produce a gsd file when he markets a Profibus slave, since a gsd file is designed to help integrate a Profibus slave to a master's configuration. In your case, Atrax never mentions a Profibus interface, and in that case I doubt you will locate a gsd file. In the Atrax website it is mentionned that the ABS960+ has "· A serial communication port for connection to computers or printer.". It is a «RS 232 port, for point-to-point communications, for which we need a bit more information, namely the protocol that runs over RS-232. https://www.atraxgroup.com/check-in-conveyor-scales/ On the PLC side, there re only 2 CP serial modules that can connect to a RS 232 bus, the CP 340 and the cP 341. To tell you which one you need, you must locate information on the protocol used to communicate with the Atrax module. It could be Modbus RTU (doubtful, it would have been mentioonned by name) or a master-slave exchange using ASCII for example. That is where you next job lies: locate that information from the vendor, from the manufacturer, from the web... Note: on the main page of Atraxgroup, Under Contacts, there is this note: "For technical and service support please contact support@atraxgroup.com..." I suggest you start with this enail to request détails on the serial protocol spécifications for the ABS960+. Hope this helps, Daniel Chartuer |
Last edited by: dchartier at: 10/22/2017 4:04:51 PM |
|
This contribution was helpful to2 thankful Users |
Follow us on