10/10/2010 7:18 PM | |
Posts: 52 Rating: (0) |
Hi All, I am using CP 343-1 (6GK7- 343-1EX30-0XE0 / v2.2)for ethernet communication is showing the BF. Configuration and Special diagnosis are attached here with. Regards, Anil AttachmentCP BF.zip (300 Downloads) |
10/12/2010 3:08 PM | |
Posts: 52 Rating: (0) |
Hi... Thanks for the reply.... Its neither the case of unplugged cable nor IP conflict. Special Diagnostics are attachedhere with.... Thanks & Regards, Anil AttachmentCP343-1.zip (325 Downloads) |
10/12/2010 3:38 PM | |
Posts: 3093 Rating: (323) |
Hello Anil, |
10/12/2010 8:32 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating: (309) |
Hello, In picture 10 you can see that there is a naming conflict. The CP can act as Profinet IO Controller/device. I suspect that the Profinet name of the CP is already in use on the network. The device name must be unique on the Ethernet subnet. Look in HWconfig. For CPs with configurable ports, there are some parameters in the properties dialogs of the PROFINET interface. Another way could be to ugrade the CP to V2.3. This can be done online. Look here: (http://support.automation.siemens.com/WW/view/en/42123315) for the changes. You will see that there is the following change: If no PN IO functionality is used, no check is made for duplicate device names. Therefore, no error LED is activated. |
Last edited by: jklm at: 10/12/2010 8:36 PMBest regards |
|