3/10/2011 6:47 AM | |
Joined: 11/18/2009 Last visit: 10/15/2024 Posts: 262 Rating: (18) |
I have connected Sentron WL via COM15 to RTU. RTU is SICAM TM 1703 ACP with Profibus. I can read all signals from Sentron without problems. But I also want to read Reason of Last trip so I can createalarm on SICAM PAC CC for each individual protection. As I can see from manual Reason of last trip is 3 bit (byte 1 bit 4,5,6) grouped together and because of that reason of last trip has 7 values (see attached PDF). In TM 1703 ACP can only read Double point or Single point. My question how is this intendedto be read? This is first time I work with Sentron. I can maybe read each individual bit as single point and than combine them and calculate value. If someone has experience with this please replay. Best Regards Ensar AttachmentPages from CommunicationManualSENTRON.pdf (374 Downloads) |
Last edited by: ensark2 at: 3/10/2011 6:54 AMLast edited by: ensark2 at: 3/10/2011 6:52 AM |
|
3/12/2011 7:28 PM | |
Joined: 11/18/2009 Last visit: 10/15/2024 Posts: 262 Rating: (18) |
Problem solved using some AND logic. |
This contribution was helpful to2 thankful Users |