8/30/2016 4:06 PM | |
Posts: 206 Rating: (22) |
Hi Arsenaly, what is the exact message you have? If you have this you can go to the manual chapter 9.5.3, here you get some hints. The manual you find here https://support.industry.siemens.com/cs/ww/en/view/109738522 . In chapter 7 you have also a procedure that guides you through the calibration process. Quite often the problem is that the calibration weight is to small or the digit difference between the calibration digits 0 and - 1 is to small. If you have load cells with 2mV/V characteristic vale the minimum calibration weight is 2% of the nominal load of all connected load cells. This corresponds to 40000 digits. The actual digits you can see in DR31. Regards ABenno |