6/27/2010 10:20 PM | |
Joined: 9/27/2006 Last visit: 5/14/2024 Posts: 12257 Rating: (2668) |
Hekki fazal; I found this decription of CEMAT modules in a CEMAT v.5 Glossary: http://support.automation.siemens.com/WW/view/en/17870163 What is CEMAT V5 ? CEMAT is a consistent, modular control system on PCS7 V5 basis with the following components that are exactly matched to each other : CEMAT ES ➩ Consistent, object-oriented engineering system CEMAT AS ➩ Open/closed-loop control and communications components for S5 / S7 CEMAT OS ➩ Redundant operator control / monitoring components and archiving components ➩ Library for all control system objects with information, diagnosis, multimedia dialogs ➩ Annunciation system with additional service functions CEMAT MIS ➩ Logging, statistics and long-term archiving system CEMAT AddOns ➩ Cement-specific process optimization applications. |
This contribution was helpful to1 thankful Users |
6/28/2010 4:10 AM | |
Posts: 2661 Rating: (279)
|
Hi fazal,
MIS stands for Management Information System equivalent to the present day MES. CEMAT used to have dedicated MIS solutions but nowadays they use (I believe) SIMATIC IT for MES. I do not think the C_MEAS_I (measured value integrator) will have it's own faceplate since this block is primarily meant for the MIS interface. For calculating the kWh from kW you can use the C_MEAS_I block by adjusting the parameters (see attachment). On the other hand you can create your own simple custom block with the following equation: Every second kWh = kWh + (nstantaneous kW/3600) Regards AttachmentC_MEAS_I_Description.pdf (123 Downloads) |
Last edited by: Phantom75 at: 6/28/2010 4:26 AM |
|
Follow us on