Hello. https://support.industry.siemens.com/cs/ww/en/view/109756832 |
This contribution was helpful to1 thankful Users |
11/26/2018 7:50 PM | |
Posts: 39 Rating: (0) |
Thanks for the link, but this is also the PCS7 version? I'm looking for the version only for Step 7, because with the PCS7 version all my projects are default set PCS7. See Default PCS7 topic. |
11/27/2018 6:02 AM | |
Joined: 8/25/2006 Last visit: 12/20/2024 Posts: 2211 Rating: (280)
|
Hello. This happens when you install Step7 and CFC from PCS7-DVD running setup from the root of DVD. To avoid this: 1. Uninstall all Siemens SW. 2. Install ALM from DVD\06_ALM__V5.x\ALM64(32)\setup.exe 3. Install Step7 from DVD\09_STEP7__V5.x\Disk1\setup.exe 4. Install CFC from DVD\10_CFC__V9.x\setup\setup.exe 5. Extract CFC 9.0 SP2 from above link without installation. Open folder with extracted files and run setup.
|
This contribution was helpful to1 thankful Users |
11/27/2018 5:06 PM | |
Posts: 39 Rating: (0) |
thx! For a complete clean I also needed to clean the register (delete all Siemens stuff). I did install CFC V9.0 without SP, because SP2 must not be used with SIMATIC S7 F Systems according to the link. |
9/4/2023 7:24 AM | |
Joined: 11/10/2021 Last visit: 8/20/2024 Posts: 1 Rating: (0) |
So helpful,Thank you! |