10/8/2020 10:28 PM | |
Joined: 9/4/2019 Last visit: 10/16/2023 Posts: 3 Rating: (0) |
Hi guys, I'd like to change the value of parameter p2000, speed reference but I can't. How is the correct procedure to change this value? Just to know, i'd like to change this value because we need to increase the speed of the machine. Could someone help me, please? ------------------------------------------------------------------------------------------ |
Last edited by: RodSchott at: 10/08/2020 22:29:19Last edited by: Jen_Moderator at: 10/09/2020 10:19:23New subject after splitting |
|
10/12/2020 9:37 AM | |
Joined: 4/28/2015 Last visit: 9/20/2022 Posts: 1278 Rating: (295) |
The maximum speed is not limited by p2000. You probably need to change p1082 if your machine does not run as fast as you want. |
Best regards, |
|
10/12/2020 3:40 PM | |
Joined: 7/7/2010 Last visit: 4/26/2024 Posts: 14639 Rating: (2349) |
I meant that if a PLC is sending speed command via telegram, 16384 is the largest value accepted, which is 100% of p2000. If 100% is being commanded, but maximum speed is not achieved, adjusting p2000 to match the maximum rpm parameter (p1082 as you stated) would allow higher speed to be attempted by the drive. If a torque or current limit were hit before max speed, then you need a different motor / drive, or change something on the load side to reduce load.
|
science guy |
|
Follow us on