Hello, For S7-1200,You can find similar discussions here: NUMBER OF PID BLOCKS IN S7-1200 PLCMax number of PID loops in S7-1214Care there limitations for PID blocks that can be used in S7 1200?The important point to add ,Proper selection of sampling rate of PID controllers can reduce the scan time of whole codes in CPU.For sluggish processes such as temperature you can increase the sampling rate up to one-tenth (0.1) of dominat time constant of process or you can try empirical values by try and error. Best regards, Hamid Hosseini |
Last edited by: hdhosseini at: 11/13/2013 11:20 AM |
|
This contribution was helpful to1 thankful Users |
11/13/2013 12:05 PM | |
Posts: 86 Rating: (3) |
Thanks alot, i'ts quite answering my question! |