9/14/2015 10:03 AM | |
Posts: 70 Rating: (1) |
Hi, I used the Go Online and the byte was almost all of the time set as TRUE without changing. Thanks
|
9/14/2015 10:25 AM | |
Joined: 11/29/2011 Last visit: 12/16/2024 Posts: 1361 Rating: (232) |
Hi, Can you please post what did you implemented. Some screenshot or a PDF printout of this part of the code. Just a note: In the SIMATIC S7-1200 Easy Book on page 73 you can read this: "Because clock memory runs asynchronously to the CPU cycle, the status of the clock memory can change several times during a long cycle." Probably that is what happens. Please upload some info about the application, and some info about the cycle times/execution times of your code. I am looking forward to hearing from you! |
Last edited by: MicroMan at: 9/14/2015 10:42:09 AM- What you read here, please check with manuals and your requirements. |
|
This contribution was helpful to2 thankful Users |
9/15/2015 6:12 AM | |
Posts: 5225 Rating: (1197) |
Thanks for the acknowledgement Jeff. Note to Siemens:
[LINK1] [LINK2] |
Last edited by: William_B at: 9/15/2015 7:21:54 AM |
|
This contribution was helpful to1 thankful Users |