1/2/2021 2:34 PM | |
Joined: 3/14/2008 Last visit: 9/13/2024 Posts: 2095 Rating: (936)
|
Hi, You are looking in the Blocks folder of your current AS project indicated by the lower left column: "Blocks" of your catalog. This means that the real comparator block is not yet existing in your project, if you go to the catalog and select "Libraries", you can go to the library where the block is listed. I think it is the CFC library or if the block exists in the master library, you can add it from there as well by drag and drop. I see you are using APL blocks , so you can even use block: CompAn02 which is a comparator of type struct real, which can handle regular Reals as well. |
Last edited by: Oreca at: 01/02/2021 14:40:40If I could help you, you can use the RATE button. Thank you. |
|
1/3/2021 11:02 AM | |
Joined: 3/14/2008 Last visit: 9/13/2024 Posts: 2095 Rating: (936)
|
Hi, See attachment...its under CFC Library\ELEMENTA\Blocks |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |
Follow us on