4/2/2012 12:15 PM | |
Posts: 3037 Rating: (192)
|
Hello, You can use the function "Rebuild All" under Project > Compiler. Or you create the Recipe View new. Do you synchronize your recipe with your plc? You must reset the area pointer "data record" after a transfer of data records. You can find more about recipe in the following manual in the chapter 8. SIMATIC HMI WinCC flexible 2008 WinCC flexible 2008 Compact/ Standard/ Advanced Tweety |
4/3/2012 12:23 PM | |
Posts: 3037 Rating: (192)
|
Hello, Which panel do you use? Tweety |
4/3/2012 3:40 PM | |
Posts: 99 Rating: (3) |
MP 277 10" Touch 1.1.3.0 |
4/4/2012 10:25 AM | |
Posts: 3037 Rating: (192)
|
Hello, You can use the job mailbox 69 and 70 for reading and writing data records. Job mailbox 69 Reading data record from PLC Job mailbox 70 Writing data record from PLC You need the area pointer job mailbox for this. You find more information in the following manual, chapter 2.4.1.7. SIMATIC HMI WinCC flexible 2008 Communication Part 1 Tweety |
5/19/2020 7:48 AM | |
Joined: 1/26/2019 Last visit: 9/13/2023 Posts: 69 Rating: (1) |
I second this error. I am also having the same issue. What is the solution to this, so we can create new, or save-as ? |