4/27/2012 12:54 PM | |
Posts: 95 Rating: (1) |
Hi All, Can anybody help with communication of PAC meters in H systems. Best Regards, JD |
4/28/2012 8:27 PM | |
Joined: 7/2/2008 Last visit: 9/30/2024 Posts: 928 Rating: (308) |
Hello JD, First, I'm not sure that PAC Profibus DP expansion module will work with PAC3100. To the best of my knowledge only PAC3200 and PAC4200 haveGSD files. Now, If you mean PAC3200. The number of PACs that can be connected under the Y-Link depends on your configuration. One PAC can send more than100 measurements but the GSD file has only 61 slots and each slot can have one measurement of 4 bytes (floating point). So, one PAC can send single measurement of 4 bytes up to 61 measurements of total 244 bytes. For example if you want to read line voltage, line current, total active power and total power factor. This means 3 voltage measurements, 3 current measurements, one measurement for total active power and one for total power factor. This gives you 8 measurements which means 32 bytes that limits you toa maximum of 7 devices per Y-Link. So, you should first know what measurements you want to read in order to know total bytes of each PAC. Best regards. H-H
|
This contribution was helpful to1 thankful Users |
4/28/2012 8:52 PM | |
Joined: 4/19/2008 Last visit: 9/3/2024 Posts: 1525 Rating: (159) |
PAC3100 Don't Support the Profibus Module, you ahve to go with PAC3200... |
Ammy |
|
This contribution was helpful to1 thankful Users |
5/2/2012 10:42 AM | |
Posts: 3093 Rating: (323) |
Hello JD, you can find the information in the manual from page 132. Regards, Kaulquappe |
This contribution was helpful to1 thankful Users |
5/20/2012 7:21 AM | |
Posts: 95 Rating: (1) |
Hello, I tried to communicate but i am facing problem.The parameters are not getting assigned?? Regards, JD |