5/21/2013 5:39 AM | |
Joined: 9/27/2006 Last visit: 5/2/2024 Posts: 12257 Rating: (2666)
|
Hello unique; The first download available in the following FAQ shows an example of Profibus communications to a MM4 drive with Load/Transfer instructions, without wholeconsistency (SFC15/14). In LAD you can use MOVE instructions instead of the STL instructions Load/Transfer. MICROMASTER 4 (MM4): Are there program examples for the Instruction Manual of the MICROMASTER PROFIBUS option module? |
Last edited by: dchartier at: 5/21/2013 5:39 AM |
|
5/21/2013 11:30 AM | |
Joined: 8/31/2005 Last visit: 4/26/2024 Posts: 2197 Rating: (326)
|
When you use PROFIBUS, why do you transfer the setpont via analouge signal? If you use PPO3, you can simply use the MOVE command to copy the data to/from drive. The sfc14/15 make shure the data consistency is larger then 4 bytes. In the attachend extract of a PDF document, you can see how to do it. The document shows how to connect a G120C to a S7-1200, but it's the same for MM4 ! I don't know if the speed reference is P20o0 in M44 too. If you use a other SIMATIC, the conversion block (Real to INT or INT to REAL) is different. AttachmentC:\Seiten aus 56749384_SINAMICS_G120C_at_S7-1200_DOKU_v10_en.pdf (133 Downloads) |
Last edited by: miami at: 5/21/2013 11:32 AMLast edited by: miami at: 5/21/2013 11:31 AM |
|
This contribution was helpful to2 thankful Users |
5/21/2013 9:59 PM | |
Posts: 14 Rating: (0) |
Actually i want to control with Temprature transmitter analog 4-20 as input to plc |
5/24/2013 8:36 PM | |
Posts: 14 Rating: (0) |
Hi dchartier , How to providerefrence value and speed for scaling my desied frequency(Hz), like 4000hex please can you explain 4000hex=100% 2000hex=50% and so on... |
5/25/2013 6:53 PM | |
Posts: 14 Rating: (0) |
|