Joined: 3/21/2006 Last visit: 9/10/2024 Posts: 10228 Rating: (1181) |
Hello Scorpioni, Your question is very common. It's deppends what kind of Siemens hardware do you have? I mean - type of CPU, CP, plus existing Siemens software. Give this information and... By the way about support, your are right. Best regards Hristo Mihalev |
4/15/2009 4:54 PM | |
Joined: 3/21/2006 Last visit: 9/10/2024 Posts: 10228 Rating: (1181) |
Hello Scorpioni, Sorry, I saw your title's thread too late.. There has ethernet way for communication with Intouch. And you can't imagine how easy is this. The decision name is DASSIDIRECT Server. And details about settings you can find in http://61.37.246.137/TECH/html/t001161.htm. Hope this will helps. Best regards Hristo Mihalev |
4/16/2009 1:21 PM | |
Joined: 3/21/2006 Last visit: 9/10/2024 Posts: 10228 Rating: (1181) |
Hello Scorpioni, So, first thing - did you start this I/O Server. Right click on ArchestraSIDI... put in start and then Auto. I guess you can ping CPU from PC.(to know that cable and physical connection is OK). ANd when you create topic in inouch, put there in "COnnection type" - DDE. You are on the right way. Just you need to "play" a little with settings. Best regards Hristo MIhalev |
Last edited by: UMENCHO at: 4/16/2009 1:23 PMAnd one more thing - your topic name must be the same like device groups from SMC (look at point 9 in to upper link). |
|
4/16/2009 3:34 PM | |
Posts: 15 Rating: (0) |
Yeehaa Communication is working splendidly now. Thank you for your support!! Greets and many thanks, Scorpioni |
4/16/2009 3:38 PM | |
Joined: 3/21/2006 Last visit: 9/10/2024 Posts: 10228 Rating: (1181) |
Hello Scorpioni, Glad to heartd this. If you have some questions in the future about Intouch let me know.... I'll try to help. Best regards Hristo Mihalev |