5/28/2010 8:34 AM | |
Posts: 382 Rating: (47) |
Hello, Well, basically I agree with Kaulquappe. These links could be helpful to you. SIMATIC S7-300/S7-400 Loadable Driver for Point-to-Point CPs: MODBUS protocol, RTU format, S7 is master SIMATIC S7-300/S7-400 Loadable Driver for Point-to-Point CPs: MODBUS Protocol, RTU format, S7 is Slave CP 441 Point-to-Point Commmunication Installation and Parameter Assignment with regards, how come |
5/28/2010 2:59 PM | |
Joined: 9/27/2006 Last visit: 4/27/2024 Posts: 12257 Rating: (2665) |
Hello samkcr; You can use a CP 341 as part of an ET 200M system, as a slave to a S7-400H system, with a loadable Modbus driver.Since you are using a S7-400H system, your I/Os should already be cofigured on ET 200M systems, so simply add the CP 341 to one of the available Et 200M systems. The following FAQ discusses how the download of the Modbusdriver to the S7-400H CPUs should be handled: http://support.automation.siemens.com/WW/view/en/17854293 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 5/28/2010 3:01 PM |
|
This contribution was helpful to1 thankful Users |
5/31/2010 10:04 AM | |
Joined: 3/21/2006 Last visit: 4/25/2024 Posts: 10228 Rating: (1181)
|
Hello, Look at Looking for a true CP341 Modbus RTU example Program .Perhaps will helps. Best regards, Hristo Mihalev |