Dear Expert's I have two S7-315-2DP PLC's with CP343-1 and both are communicating over Ethernet. Now I have one mmore newsystem with S7 314-2PN/DP PLC, how can i exchange data between this and one of above 315-2DP PLC. Can i use MASTER/SLAVE Communication or Can I use Global Data connection. Plz suggest the simplest and best way to do..... Except : http://support.automation.siemens.com/WW/view/en/6518822 This is example with s7 400 one side and s7 300 other side. But in my case both are s7 300. Thanks & Regard\s |
Naveen Paliwal |
|
10/14/2013 12:15 PM | |
Joined: 4/19/2008 Last visit: 11/21/2024 Posts: 1525 Rating:
|
Hello , If new Added CPU 314 in the Same Ethernet Network then You can Used the "USEND/URCV", BSEND/BRCV, "PUT, GET" Block In the Below Mention Manual Page No. 95 you will find the Detail about the Which Block used during which Combination. CPU-CPU Communication with SIMATIC Controllers |
Ammy |
|
10/14/2013 12:17 PM | |
Joined: 1/28/2009 Last visit: 4/22/2025 Posts: 6867 Rating:
|
Hello, It depends on if you have PROFIBUS subnet on the DP integral port in the mentioned CPUs and what is the role of that CPUs in that subnet.If there is no network defines, you can set a new subnet.Define one of the CPUs as master and the other(s) as slave and configure the communication.More data available here:
If both CPUs are master in different PROFIBUS subnet, you can try communication over MPI via global data communication. I hope these comments help you Hamid Hosseini |
1/14/2016 9:41 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating:
|
New question published by autoz699 is split to a separate thread with the subject 314c 2dp, backup without mpi port. Best regards |