5/17/2012 10:09 AM | |
Joined: 9/28/2005 Last visit: 10/22/2024 Posts: 2957 Rating: (242)
|
Lets wait for original user. |
Best regards, |
|
5/17/2012 11:21 AM | |
Posts: 20 Rating: (0) |
Hello, Please check the attached hardware configuration and connection diagram. Regards |
5/17/2012 7:41 PM | |||
Posts: 559 Rating: (87) |
Dear jass, For S7-200 PLC it is not possible to communicate HMI & PC together on the same port. If one port is engaged for one application, it can't be use for another application. My suggestion is that you should go for 224 XP or 226 which have two ports available, So one can be used for programming/monitoring purpose & another can be used for HMI. |
||
This contribution was helpful to2 thankful Users |
5/18/2012 2:42 PM | |
Posts: 153 Rating: (2) |
SolutionctFinder is correct.. |
This contribution was helpful to1 thankful Users |