10/28/2015 7:52 AM | |
Joined: 3/21/2006 Last visit: 4/25/2024 Posts: 10228 Rating:
|
How do you configure and program an S7 connection and the FB15 "PUT" und FB14 "GET" function blocks for data transfer between an S7-1200 CPU and an S7-300 CPU?The above written FAQ will not work in your hardware. S7- connection will not be possible to configure it in S7-300. So, you create the connection and programming (PUT and GET) in the S7-1200 cpu.Follow the manual from the next post.
|
Last edited by: UMENCHO at: 10/28/2015 8:03:21 AM |
|
This contribution was helpful to
1 thankful Users |
10/28/2015 7:52 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
|
Hi SdSady, See the following manual how to do it. CPU-CPU Communication with SIMATIC ControllersAs you see on page 97, the communication should work with Open Communication or S7-Communication with the S7-300 as Server(for PUT/GET). hope this helps, regards, |
FCK WAR! |
|
10/28/2015 7:53 AM | |
Joined: 7/9/2015 Last visit: 7/17/2024 Posts: 3874 Rating:
|
Hi,
here are some links with Application examples for comunication:
How can you have two online connections between STEP 7 V5.5 and an S7-300 and between STEP 7 V11 and an S7-1200 side by side? https://support.industry.siemens.com/cs/de/en/view/50572734
How do you configure and program an S7 connection and the FB15 "PUT" und FB14 "GET" function blocks for data transfer between an S7-1200 CPU and an S7-300 CPU? https://support.industry.siemens.com/cs/de/en/view/92269951
Hope this will help you! There are many more examples on the siemens support homepage. Regards, Towome |
|
|
10/18/2018 9:13 AM | |
Posts: 1 Rating:
|
The attached document explains how to create the communication between the 1214C CPU and the 315 2DP via the CP 343-1 : WORK SWEET ! AttachmentConnexion 1214C to 315 2DP via 343-1 Lean.pdf (2805 Downloads) |
This contribution was helpful to
8 thankful Users |
Follow us on