6/4/2019 9:49 AM | |
Joined: 9/9/2015 Last visit: 6/24/2024 Posts: 727 Rating:
|
Dear all, I faced an issue today on Full OS compilation on PCS 7 V9.0 SP1. The error message is An error has occurred updating the group messages. After troubleshooting, I found out the reason. It is because I deleted all the block group which I previously set to hide all the Smart Alarm Hiding.
For example, I hide messages by 1. inserting StRep A, 2. rename the block group to TEST. 3. Then I set all the block group to TEST for OCM blocks. 4. Then I tick the hiding in the POV. 5. Compile OS. Then test completed. I removed all the Block groups and insert/create new StRep for another type of block group. After deleted all the block group named "TEST" to empty and do a full OS compilation, this message of "error has occurred updating the group messages" occurred. SOLUTION After multiple attempts, the error was resolved by 1. inserting another StRep with empty block group and 2. at the POV, click on the block group, select the empty selection using the drop list and 3. do a Full OS compilation. Issue resolved and attached with a picture for future reference. |
Please give me 5 stars Rating if my post is helpful for you. :) |
|
This contribution was helpful to
3 thankful Users |
6/4/2019 10:07 AM | |
Joined: 3/14/2008 Last visit: 7/12/2024 Posts: 2076 Rating:
|
Thank you for the tip |
If I could help you, you can use the RATE button. Thank you. |
|