5/13/2011 2:51 AM | |
Joined: 9/27/2006 Last visit: 9/21/2024 Posts: 12282 Rating: (2684) |
Hello gentlemen; Faz favor de usar o idioma ingles nas proximas perguntas nesse foro. Obrigado. For those of us in the forum who might be interested in the subject, but who do not have the chance to speak Portugese, here is a quick translation of the posts above: Question from scopel_rs :Good evening; I would like to know how to control 10 frequency inverters MM430 (speed and Run/Stop) with a PLC S7-1200, with a HMI panel to set these values. Thank you. Replyfrom Mr. Kataoka.: Hello; It is true that with USS communications for example you can control up to 16 MM. I wiil give you a link to an application developed for a S7-1200 with a G110.With a few changes you will be able to communicate between a S7-1200 and a MM430 .https://support.automation.siemens.com/BR/llisapi.dll?func=cslib.csinfo&lang=pt&objid=40157517&caller=view Note: A new communication module and the firmware that allows the S7-1200 to communicate over Profibus have just been launched, a new possibility for your application. Using TIA v. 11 (S7-1200-Profibus-MM440): /tf/WW/en/Posts/57694#top Please do not hesitate to rate this post. Regards, Mr.Kataoka |
Last edited by: dchartier at: 5/13/2011 2:53 AM |
|
This contribution was helpful to2 thankful Users |