Hello David, firstly check taking the correct connection makro CN011 (Modbus RTU). Then send in STW1 047E hex. By changing to 047F hexthe drive should switch on and turn with the value sent as setpoint. Please find section 5.5.1.3. and6.2. in the V20s manual. (http://support.automation.siemens.com/WW/view/en/67267484) |