5/10/2013 9:49 PM | |
Posts: 90 Rating: (7) |
Config 2 see attached file |
5/11/2013 4:50 PM | |
Joined: 10/7/2005 Last visit: 11/18/2024 Posts: 3027 Rating: (1057)
|
Hello Ariya Man sorry, your solution will NOT work and you MUST use two IM153-2's AND active backplane modules for the ET200M for your Software Redundant System. Have a look atWhich modules can you use when implementing software redundancy? to find out which modules you can use andI also suggest you study the SIMATIC S7-300/S7-400 Software redundancy for SIMATIC S7 manual for all the other helpful nitty gritty details on this subject. I hope this helps |
Cheers |
|
This contribution was helpful to1 thankful Users |
5/12/2013 2:36 PM | |
Posts: 90 Rating: (7) |
Thanks fritz, so you mean I need to add another IM 153-2 to our configuration (Config 2) and it works fine? |
5/12/2013 3:35 PM | |
Joined: 10/7/2005 Last visit: 11/18/2024 Posts: 3027 Rating: (1057)
|
That is correct dear Ariya Man |
Cheers |
|
This contribution was helpful to1 thankful Users |
7/9/2013 7:11 AM | |
Posts: 93 Rating: (13) |
Yes only one IM needs to be added . apart fomr that the configuration is ok. RKM. |