1/12/2012 10:51 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating:
|
Hello, The SF led blinking is because the settings are wrong or/and connections are bad or there are no sensors connected at al. The first 5 switches are default off, for use with pt 100, if you have other type off sensor see attached part of manual for settings. Switch 6 is what value you get in case of wirebreak -3276.8 (on) or +3276.7 (off). Switch 7 is Degrees F(on) or Degrees C(off). Switch 8 is 3 (off)or 2/4 wire (on) Unused channels should bebridged with a resistor. Regards, Marcjan Attachmentrtd-module.pdf (376 Downloads) |
Last edited by: Marcjan at: 1/12/2012 10:53 AMProblem solved? |
|
12/16/2013 6:30 AM | |
Joined: 12/11/2013 Last visit: 9/16/2023 Posts: 1 Rating:
|
What are the settings in case of K type Thermocouple??? Thanks in advance
|
12/16/2013 7:24 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating:
|
Hello, Please have a look at attached part of manual, Table A-27. regards, Marcjan Attachments7200_system_TC-part.pdf (253 Downloads) |
Problem solved? |
|
This contribution was helpful to
1 thankful Users |